16

Do electrical boxes have to be flush to the finished surface? Can they recess any depth into the wall by as much as 1/8" or 1/4"?

Edit: I appreciate everyone offering alternative solutions to making a non-flush, already-installed box flush to the finish, but remember that I am looking for an objective answer regarding whether or not the box has to be flush to the wall. This is new work, so if I can get by with having it recess into the wall by 1/8" or 1/4" then I will do so. Otherwise, I will have to alter my plans.

Tester101
  • 133,087
  • 80
  • 327
  • 617
oscilatingcretin
  • 5,932
  • 53
  • 99
  • 114

3 Answers3

20

They make box extenders (an example is depicted below) that can be used to extend boxes to meet the finished surface.

a non-metallic box extender of the telescopic type

The 2014 NEC says...

ARTICLE 314

Outlet, Device, Pull, and Junction Boxes; Conduit Bodies; Fittings; and Handhole Enclosures

314.20 In Wall or Ceiling. In walls or ceilings with a surface of concrete, tile, gypsum, plaster, or other noncombustible material, boxes employing a flush-type cover or faceplate shall be installed so that the front edge of the box, plaster ring, extension ring, or listed extender will not be set back of the finished surface more than 6 mm (1⁄4 in.). In walls and ceilings constructed of wood or other combustible surface material, boxes, plaster rings, extension rings, or listed extenders shall be flush with the finished surface or project therefrom.

This might also be relevant.

406.4 Receptacle Mounting. Receptacles shall be mounted in boxes or assemblies designed for the purpose, and such boxes or assemblies shall be securely fastened in place unless otherwise permitted elsewhere in this Code.

(A) Boxes That Are Set Back. Receptacles mounted in boxes that are set back from the finished surface as permitted in 314.20 shall be installed such that the mounting yoke or strap of the receptacle is held rigidly at the finished surface.

Tester101
  • 133,087
  • 80
  • 327
  • 617
12

Since you say new construction you can get adjustable boxes if not from a big DIY box store then you can get them from an electrical wholesaler.

Adjustable box

If you use the box extender make sure what you buy has a UL on it, or whatever country you live in stamp of approval.

Here's the spec sheet on the adjustable box. Here.

lqlarry
  • 7,617
  • 1
  • 20
  • 37
-3

All you have to do is use a cheap plastic nail on box, cut the plastic off that holds the nail, and fasten it with 2 drywall screws from the inside of the box.

Niall C.
  • 20,909
  • 19
  • 95
  • 135