I just moved into a new house where there are two 240 volt 10-30R outlets in the garage, each with a 30-amp breaker and 10 gauge wire. Voltage across the hot terminals is 247 and, of course, approximately 124 volts from each hot terminal to neutral. So far, so good. However, on both outlets, the voltage across the metal face plate to either of the hot terminals is 14-18 volts. Why the heck is that? There is a bare ground wire in each of the boxes, but there is no ground terminal on the 10-30R receptacle, so the ground wires are just pushed to the back of the boxes. Where the heck is that voltage on the face plates coming from? And is it a safety problem?
Asked
Active
Viewed 126 times
1 Answers
4
You have grounds in the boxes.
So.
- Buy two 14-30Rs
- remove the 10-30Rs
- connect the 14-30Rs
- Smash the 10-30Rs with a hammer so they don't get re-used
- place in trash or recycling.
Per comment about "3-wire compressor & welder": alternatively L6-30R Plus L6-30P for the cords, and cap the neutral while connecting the ground.