How many cables are you allowed to run through a single hole in a wooden floor joist?
We have a question and good answers for the NEC guidelines. Why would an inspection company flag this and note that there is an "overheating" chance?
Note that these wires are on the same circuit and oversized (just going to canned lights).
Is there any new guidelines I am missing here?
DMoore
  • 50,637
  • 93
  • 208
What they're probably trying to flag...
The usual thing that gets cited for this is the second paragraph of NEC 334.80 (text from 2017, but this hasn't changed much -- 320.80 is a newer extension of it that applies to AC/BX):
Where more than two NM cables containing two or more current-carrying conductors are installed, without maintaining spacing between the cables, through the same opening in wood framing that is to be sealed with thermal insulation, caulk, or sealing foam, the allowable ampacity of each conductor shall be adjusted in accordance with Table 310.15(B)(3)(a) and the provisions of 310.15(A)(2), Exception, shall not apply.
...and why their cite's a swing and a miss
However, even though the 24" exception (which is the exception cited in the quote above) is ruled out in this case, because ampacity adjustments on NM cables are permitted to be made from the 90°C column ampacity in the table by the first paragraph of that very same section:
The ampacity of Types NM, NMC, and NMS cable shall be determined in accordance with 310.15. The allowable ampacity shall not exceed that of a 60°C (140°F) rated conductor. The 90°C (194°F) rating shall be permitted to be used for ampacity adjustment and correction calculations, provided the final calculated ampacity does not exceed that of a 60°C (140°F) rated conductor. The ampacity of Types NM, NMC, and NMS cable installed in cable trays shall be determined in accordance with 392.80(A).
As a result of that fact, we can start with the 25A 90°C ampacity of 14AWG copper (or the 30A figure for 12AWG copper), and then start adjusting it accordingly, based on the number of cables (really, current-carrying conductors) we have present:
  • 3 /2 cables (6 CCCs): 80% adjustment, so 20A > 15A (or 24A > 20A)
  • 4 /2 cables (8-9 CCCs): 70% adjustment, so 17.5A > 15A (or 21A > 20A)
  • More than that: 50% adjustment, so 12.5A < 15A = now the adjustments limit ampacity
So, unless you're cramming 5 cables (whether /2 or /3, in most cases) into a single hole, or using archaic cables that lack 90°C rated insulation (all modern NM is NM-B, which means that the wire insulation is 90°C rated), then you're good to go.
ThreePhaseEel
  • 87,685
  • 144
  • 243
I believe the inspector may be interpreting the new 320.80.A wrong. When more than 2 armor clad cables are bundled together and installed so they are in contact with thermal insulation, calk, or sealing foam, and an air gap is not maintained between those cables to dissipate heat the ampacity of each conductor shall be adjusted according to table 310.15.C.1.
I asked the question why not 3 or more because 8 CCC of nmb, ac, mc will all still meet code for ampacity because they are all 90 deg rated. The person came back with what if they are not 90 deg I said check code they are required to be in the articles covering these wiring methods he then was stuck.
So make them cite it to write it, call your local building codes office and ask as this is probably being wrongly remembered as my comment above was wrong but I remembered bundling BS as I said.
Ed Beal
  • 103,727
  • 79
  • 158