Original Question
I was extending a circuit in my kitchen last week as part of a remodel and discovered something that had been under my nose the whole time I've lived here but I just paid enough attention to notice.
There are 5 multiwire branch circuits in my main panel (6 if you count the one I added), and only 1 of them (2 if you count the one I added) was handle-tied. Additionally, all of them have at least one leg (sometimes both) on double-stuff breakers.
Now, I know I need to fix this and it will involve moving at least 4 circuits around, probably more since I'll likely need to shift a few others just to get enough adjacent spaces.
My question is: When did handle tying a MWBC become code?
This house was built in 2010 in Riverside County CA, so the code in force would have been either the 2010 CA Electric Code (which adopts 2008 NEC) or the 2007 CA Electric Code which adopts 2005 NEC). Everything in that panel aside from the three 2-pole breakers at the top is original. They did put a couple AFCI breakers in for the bedrooms, so they were sort of on the ball. I don't know why thy used almost all tandems in a brand-new panel that only ended up just over half full. (Those 3 double poles at the top were added recently by me).
At least they got the poles on the right busses (hopefully on the first try) even though they aren't anywhere near adjacent. For example, the MWBC that serves 2 of the kitchen circuits is half on the bottom of the quad and half on a full-size single pole 3 spaces up. I've added colored tape patches to mark which circuits are MWBC.
Finally: when I fix this, since I will be moving circuits in this panel and possibly relocating 1 or 2 to my subpanel to make room, will I need to comply with the current code (2019 CEC/2017 NEC locally) and AFCI all the things? (If that's the case, it might become costly enough to justify seeing if I can find QO innards that fit this enclosure since I'll be replacing more than half the breakers anyway.)
Update Feb. 2023
I went ahead and moved a bunch of lower load circuits to another panel, leaving enough room here to put everything on double poles. Common trip technically unnecessary of course, but turns out finding double pole breakers was cheaper and easier than finding handle ties for the teeny ones.
Now nobody will get bit in the future servicing the MWBCs, and as a bonus, I can get an amp clamp around anything without having to dig.