3

I wired two circuits for dryer and water heater. I installed an electrical box on the wall right above the electrical panel, fished NM 10/3 and NM 10/2 through the wall, and run 5 THHN #10 wires in a 1/2'' EMT.

Because the wall is between the house and the garage I wanted to avoid making a big opening, installing the box flush to the wall and having a box extension for the EMT conduit. So I decided to install the box on top of the wall, run the NM cables in two holes and fire block just the two holes.

But I forgot to do a box fill calculation so I had to install a box extension after all... Having 10 conducting wires of gauge 10, NM connectors (this which I think counts as internal and this which should count as external), and 2 grounding wires requires 30 cu in. In retrospect I should had installed a deep square box of 30.5 cu in instead of the current one that is 21 cu in. To satisfy the minimum box fill volume I added an extension box and now I'm at 41 cu in so I'm good. But it looks weird and ugly. Am I violating any code with this setup? I'm in California. Are there any other smaller box extensions I could use that would give me the 9 cu in I'm missing?

If you notice any code violations from the pictures below please let me know.

Box above the electrical panel with two NM cables fished behind the wall and EMT conduit going to the next box:

enter image description here enter image description here enter image description here enter image description here

Box above existing dryer outlet with NM cable fished behind the wall going to the outlet below and with liquidtight whip attached on the left for the water heater:

enter image description here enter image description here enter image description here

Dryer outlet that replaced a NEMA 10-30R:

enter image description here enter image description here

Changed the wiring on the dryer to 4 wires:

enter image description here

Electrical sub panel: I capped the 2 hots of the previous dryer wiring with a wire nut, installed two Raco the insider NM connectors for the two orange NM cables, replaced the old handle-tied 30A breakers for the dryer with a new GFCI 30A breaker, and replaced two 15A breakers with a 4-pole quad circuit breaker to get 30A for the water heater.

enter image description here enter image description here

Electrical sub panel photos before I did any work. I had to move some breakers around to move the tandem breakers at the bottom and also make space for the water heater breaker.

enter image description here enter image description here

For completeness, main panel from top to bottom: solar, EVSE, air handler, heat pump, service disconnect, surge protector, power meter for EVSE load management, subpanel, driveway lights and plug.

enter image description here enter image description here

user162793
  • 452
  • 3
  • 16

2 Answers2

6

The extension box to meet fill volume is code legal. Since you seem to have the clamps outside the box, your fill is only 27.5" there - up to 4 grounds count as one, before you need to start adding 1/4 of wire fill for the 5th and beyond. (NEC 2020 and beyond.) So you have 10 conductors + 2 grounds that count as 1, for a total fill count of 11, or 27.5". If you had internal clamps (which I don't see) you'd need another count for those and be at 30 c.i. If you didn't clamp the NM cables, that would be a violation and need to be corrected.

If you don't like the extension box you can choose a larger box, such as a 4-11/16 x 4-11/16" (at 29.5 c.i. for a 1.5 inch deep box, 42 c.i. for a 2-1/8) or a 4 x 4 x 2-1/8 for 30.5 c.i. - or you could use a blank exposed work cover of at least 6 c.i. capacity (so, a raised cover) to bring a 4 x 4 x 1.5 from 21.5 c.i. up to 27.5 c.i. or more. Most 1/2" raised 4x4 covers are rated 6.5 c.i. so those would get you to 28 c.i. for the box+cover.

Ecnerwal
  • 235,314
  • 11
  • 293
  • 637
4

But it looks weird and ugly. Am I violating any code with this setup? I'm in California. Are there any other smaller box extensions I could use that would give me the 9 cu in I'm missing?

Nope, that's legit. You can do that a couple more boxes tall if you want to. (there's a limit before you violate 110.12 "Neat and Workmanlike", but it's a judgment call.)

Anyway, your cubic inch problem is why 4-11/16" boxes are my automatic go-to anytime I have the slightest concern with cubic inches. At 42 cubes they can't be beat. Unfortunately it's not really compatible with the big-box store life, since (oddly) they don't specialize in big boxes, and you'll go broke paying their obscene prices. (this is true on a lot of things actually - "Save Big Money" is a shameless lie). I get my 4-11/16" at a friendly electrical supply. And if that's too awkward a name, try "120mm".

If you notice any code violations from the pictures below please let me know.

Right off the bat I see red wires on single-pole breakers in the tandem groups. These are probably Multi-Wire Branch Circuits aka shared-neutral circuits. 2 hots 1 neutral, altogether counts as 1 circuit. The hot wires must be phased very carefully or neutral will be overloaded and tandems encourage tragic mistake. Further, modern code requires MWBCs be handle-tied so that a maintainer is forced to turn off the entire circuit. (the handle-tie requirement tends to enforce correct phasing, since you can't stick a handle tie between the two handles on a tandem).

So I would go ahead and trace those red wires to their cable, identify their partner black wire and trace them back... untangle and tape them together to make it more obvious they are associated, and make sure those two are on a pair of breakers that are handle-tied. A quadplex is an acceptable form of handle-tie (it provides common trip which is overkill for a MWBC with only 120V loads*, but that's fine). Siemens sells appropriate handle-ties to go between tandems.

Where is your main breaker? Because first, I'm really weirded out that a whole house will fit on a 16-space panel, but second, maybe it's a trick of the light, but this panel really, really looks like a Split Bus / Rule of Six panel where the "Main Breaker" is actually the "up to six" breakers in the Main Breaker area. On a 16-space split-bus, those are done as 8 main breaker area spaces and 8 "Lighting Area" spaces (which are fed from a breaker in the Main Breaker area, presumably the 40A). These panels have two problems. First, nothing except the NEC Article 220 Load Calculation prevents overload and nobody ever re-does their 220.82 Load Calculation when they add stuff. And second, if the 40A breaker feeds the lower half, that's way too much stuff for a 40A breaker to support. Maybe I'm mistaken.

Changed the wiring on the dryer to 4 wires:

Make sure you followed the procedure in the manual. What I'm particularly concerned with is removing the neutral-ground bonding jumper. Unplug the dryer and measure resistance between neutral and ground. If it's infinity, you're all set.

I capped the 2 hots of the previous dryer wiring with a wire nut

If the wiring at the dryer end is in a state where it can be reused for a load that doesn't require neutral (e.g. EV charging, heat pump dryer, ??? future load) then that's fine. However if it's destroyed beyond use at the dryer end, it must be destroyed beyond use at the panel end also.




* Am I implying MWBCs can also support 240V loads? Yeah.