-1
I have 4 cables from a power supply which are 3 phase WYE 208 volt. so if I measure between neutral and hot I get 120V.
The problem is that I need to hook up a compressor for 110V single phase (just normal wall socket) to this particular combination.
Question 1: Is this just a bad idea to begin with since the phases are 120deg apart instead of 180? If it is is there some gadget I can buy to convert correctly?
Part 2: My attempt: so I tried to hook it up and I soldered the neural to the ground of a cut 3 prong extension cord, the I soldered a hot wire to the small and large hole of the plug. This was a bad choice because after I ran the compressor I triggered the circuit breaker. Then i realized that i was feeding it 240V instead of 110V.
Question 2: Do you think I should try to leave the ground on the prong open and instead solder the neutral to the small hole and one of the hot wire (does it matter which) to the big hole. This way I would supply the compressor with 110V?
As far as I understand, it doesn't matter now that the phase is 120 between the hot wires, because I am using neutral to hot, right?
Zlatko-Minev
  • 111
In a 208Y/120 4 wire Wye system, you'll get 120 volts between either ungrounded (hot) conductor and the grounded (neutral) conductor. So if you're trying to connect a 120V appliance, all you need is one ungrounded (hot) conductor, one grounded (neutral) conductor, and one equipment grounding conductor.
The ungrounded (hot) conductor will connect to the brass colored screw terminal on devices (the small hole/blade), while the grounded (neutral) conductor will connect to the silver colored terminal (the larger hole/blade). The neutral conductor should never be connected to the equipment grounding conductor, or equipment grounding terminal on devices.
Notes:
Since it sounds like you're a bit over your head, you should probably contact a local licensed Electrician to finish the project and for any future electrical projects.
While you can solder connections in house wiring, it's not a common practice anymore. You'll also want to insure that you are using solder that is rated and labeled for the use, and that your solder joints are strong and insulated.
all connections must be made with listed pressure connectors (wire nuts) are the standard , code specificly states that connections cannot be made by solder alone. other than that the others that weighed in on the grounding issue are correct, you dont want an alternate ground path that could energise the rest of your house including making "ground loops that can dammage switching powersupplys used in computers and most new TV's and electronic devices
Ed Beal
  • 103,727
  • 79
  • 158