This is not a question about whether it is in code, or safe to wire a 110 outlet with its neutral to the ground of a 240 circuit. I accept that it is unsafe, and it's certainly not up to code, I'm trying to get my head around what makes it unsafe. What exactly could happen with this type of bad wiring?
4 Answers
Neutral is not ground. Neutral is the desired current return, ground is a safety device only.
Let's look at some fault conditions, and we'll lead up to the problem with the bootleg ground. First, consider a broken neutral wire (near the service panel) with no loads on the circuit whatsoever.
Nothing is connected to the neutral; it's floating. That's not the same as being at zero. Nothing pulls it down to zero (neutral) but nothing pulls it up to hot either.
But what if something did?
This is concerning. You see the broken neutral is being pulled up to 120V. Not toward 120V - all the way, because absolutely nothing pulls it down to real neutral. This is deadly if you have a NEMA 10 dryer or stove circuit, where they intentionally attach chassis to neutral as a substitute for ground. But other than that, this situation is not that hazardous if everything is perfect and to code, and probably wouldn't even trip a breaker. And since neutrals stay with their mated hots, this problem is contained to a single circuit.
Now to your hypothetical: a bootleg ground. Same, but substitute ground for neutral.
Holy smokes! We've now lit up every ground downstream of the break. Unlike neutrals, grounds may be cross-connected, so it can affect every circuit. Every screw in every outlet cover, any metal conduit, any appliance which properly grounds its chassis (particularly NEMA 14 connected dryers and stoves), the exterior of your metal power strips, maybe even the chassis of your PC.
In fact a single point of failure - the ground-neutral bond in your main panel - combined with a bootleg ground, will create the worst case scenario: energizing every ground in your house including the service panel itself.
Other than that, I see ground breaks all the time - especially in EMT conduit, where those flimsy zinc couplers can snap off.
Here's why the grounding rod won't help. Dirt is a lousy conductor, except when it's not. Grounding is done to force the house's ground system (and neutral) to be near earth, to reduce shock hazard. It's not meant as a current return, and it works so badly as one, that using it that way creates the hazard!
Power wants to get back to neutral, not ground. The only place ground can reach neutral is back at the transformer pole, and that current path goes through unreliable dirt. Code says a single ground rod must be 25 ohms (but if you have two, you don't even have to test! This is because of the practical difficulty of getting good earth connections in some places.) Run the math: E=IR, 120V=4.8A*25Ω. In other words a dead short would flow 4.8 amps. That's not going to trip a breaker, and can't be counted on to reduce shock hazard from that bootleg ground. The bootleg load could be considerably less than 25 ohms, so it's going to pull ground up toward 120V better than earth may pull it down.
I know it's a busy drawing, click to zoom. Here's what else is going on there: High voltage 3-phase delta (yellow orange brown) feeds a single-phase neighborhood transformer, whose secondary is 240 volts center-tap. The center tap is Neutral, and it's bonded to a grounding rod at the transformer. Those 3 wires, hot-neutral-hot, are bundled together and carried to each house via its meter. Each house has a grounding rod bonded to ground, which is also bonded to neutral in the main panel.
- 313,471
- 28
- 298
- 772
Electricity follows every available path back to the source. If you connect neutral to ground, you're putting current on the grounding conductor. This includes conduit, boxes, device chassis, enclosures, bare (uninsulated) wire, etc. If a person comes into contact with any of those devices, they can become a path as well.
This can lead to injury, and/or death.
- 133,087
- 80
- 327
- 617
The risk of a bootleg ground is that grounded devices can become energized and potentially lethal to touch should the neutral connection ever fail or simply have too high of a resistance.
To give a sample scenario, suppose you have an electric heater on a circuit that uses a bootleg ground. And downstream of that bootleg, the neutral goes through an old outlet where the neutral connection finally fails in a chard mess that luckily doesn't light the house on fire. The heater stops working, you pick it up to see if you can see why. And to get a better look, you flip the light switch. When you touch the screw on the light switch, you have up to 120v and a whole lot of amps going in the hot of the heater, out the neutral, through the bootleg ground connection, back out to the grounded metal casing of the heater, through your body (eek), and back out to the grounded screw on the light switch.
- 43,263
- 15
- 98
- 204
The whole point of grounding devices and other conductive parts inside an structure is to establish effective ground fault detection. Circuits normally feed multiple appliances and while not readily obvious, rely on a clean, zero potential reference to ground in case an actual fault to ground occurred.
Why this is really dangerous
The obvious reason is someone can get shocked, especially electricians working on the system. This is because a non-current carrying conductor ( the ground ) is now carrying current on a regular basis for which it is not designed to do.