For example, I have a 12/3 cable in which the red and black wires are controlled via separate breakers. The 12/3 drops into a single-gang outlet, out of which runs a 12/2 to another room. Is there a word/term for this (joined circuit, sistered circuit)?
I'm looking for a polite term ;)
(EDIT: Changed /4, /3 to /3, 2 - all cables mentioned contain grounds)
overslacked
  • 407
From Wikipedia
Split phase shared neutral (North American Wiring)
In split phase house wiring, for example, a duplex receptacle in a kitchen is typically connected with a cable that has three conductors, in addition to ground. The three conductors are usually colored red, black, and white. The white serves as a common neutral, while the red and black each feed, separately, the top and bottom hot sides of the receptacle. Typically such receptacles are supplied from a ganged breaker, i.e. a breaker in which the handles are tied together for a common trip, so that if one kitchen appliance malfunctions and pops the breaker, the other side of the duplex receptacle will be shut off as well. This is called a multiwire circuit.
Notes:
These types of circuits must use a double pole circuit breaker
While the NEC recognizes this configuration, there is open debate as to weather or not this is a safe practice. For more information see Understanding the Dangers of Multiwire Branch Circuits
EDIT
Multiwire circuits for 3 and 4-way switches
Switch legs, also called travelers must now be in a different color to be easily identified. A few years ago the white wire could be used as a traveler but code changed that to lessen the confusion of identifying the traveler. Now instead of running a piece of 14/2W/GRD or 12/2W/GRD for 3-way you have to use 14/3W/GRD or 12/3W/GRD. Same goes for 4 Way's also.
It sounds like a poor man's 220. Are the breakers next to each other vertically in the box? If so, then black is carrying 110 from one line, and red is carrying 110 from a second line.
Strictly speaking those lines should be fed into a single double throw breaker which covers two posts in the box.
The Evil Greebo
  • 25,971
  • 91
  • 125