21

I have the 2 circuits in the kitchen with GFCI outlets, but I'm not quite sure which other ones do NOT need GFCI. Other circuits in the kitchen include Microwave, Fridge, and Dishwasher. It makes sense to me to not have the fridge on GFCI though.

auujay
  • 5,315
  • 15
  • 44
  • 55
rcav8r
  • 259
  • 1
  • 2
  • 4

4 Answers4

15

The NEC (NFPA 70 2011 edition) requires GFCI receptacles in kitchens of dwelling units where the receptacles are installed to serve the countertop surfaces. It does not mention a distance requirement in kitchens.

The distance requirement of 1.8 meters (6 feet) is for sinks located in areas other than kitchens.

Section 210.8 A of NFPA 70 2011 Edition deals with GFCI protection in dwelling units (see below).

210.8 Ground-Fault Circuit-Interrupter Protection for Personnel.

Ground-fault circuit-interruption for personnel shall be provided as required in 210.8(A) through (C). The ground-fault circuit-interrupter shall be installed in a readily accessible location. Informational Note: See 215.9 for ground-fault circuit-interrupter protection for personnel on feeders.

(A) Dwelling Units. All 125-volt, single-phase, 15- and 20-ampere receptacles installed in the locations specified in 210.8(A)(1) through (8) shall have ground-fault circuit-interrupter protection for personnel

(1) Bathrooms

(2) Garages, and also accessory buildings that have a floor located at or below grade level not intended as habitable rooms and limited to storage areas, work areas, and areas of similar use.

(3) Outdoors
Exception to (3): Receptacles that are not readily accessible and are supplied by a branch circuit dedicated to electric snow-melting, deicing, or pipeline and vessel heating equipment shall be permitted to be installed in accordance with 426.28 or 427.22, as applicable.

(4) Crawl spaces — at or below grade level

(5) Unfinished basements — for purposes of this section, unfinished basements are defined as portions or areas of the basement not intended as habitable rooms and limited to storage areas, work areas, and the like
Exception to (5): A receptacle supplying only a permanently installed fire alarm or burglar alarm system shall not be required to have ground-fault circuit-interrupter protection.

Informational Note: See 760.41(B) and 760.121(B) for power supply requirements for fire alarm systems.

Receptacles installed under the exception to 210.8(A)(5) shall not be considered as meeting the requirements of 210.52(G).

(6) Kitchens— where the receptacles are installed to serve the countertop surfaces

(7) Sinks — located in areas other than kitchens where receptacles are installed within 1.8 m (6 ft) of the outside edge of the sink

(8) Boathouses

RSMoser
  • 806
  • 5
  • 6
11

All outlets that support convenience plug in items within 8 feet of a water source must be GFI protected. However, the new NEC calls for a separate non GFI circuit (home run) for the fridge or other fixed appliances. These non protected circuits must be single purpose and wired to a single outlet or direct wired and dedicated to the appliance. This can include dishwashers, garbage diposers, vent fans, most permanent motor loads.

Tester101
  • 133,087
  • 80
  • 327
  • 617
shirlock homes
  • 58,628
  • 3
  • 87
  • 168
6

According to the 2014 version of the National Electrical Code, all 120 volt, single phase, 15 and 20 ampere receptacles in dwelling units, serving coutertop surfaces are required to have ground-fault protection for personnel.

So any other kitchen receptacle, would not require GFCI protection.

National Electrical Code 2014

Chapter 2 Wiring and Protection

Article 210 Branch Circuits

210.8 Ground-Fault Circuit-Interrupter Protection for Personnel.

(A) Dwelling Units. All 125-volt, single-phase, 15- and 20-ampere receptacles installed in the locations specified in 210.8(A)(1) through (10) shall have ground-fault circuitinterrupter protection for personnel.

(6) Kitchens— where the receptacles are installed to serve the countertop surfaces

Tester101
  • 133,087
  • 80
  • 327
  • 617
-4

Another reason the NEC probably didn't require GFCI on dedicated appliances like refrigerators and dishwashers is that many manufacturers had previously connected the neutral and ground wire together in which some electrical current may return to the source through the ground wire tripping GFCIs. I believed UL required this at one point. I don't know if newer appliances still have this.

Most electrical fixtures and appliances these days are double insulated and usually don’t have a problem. Just be aware that not all 3-wire appliances will work properly when directly plugged into a GFCI circuit.

Tom S
  • 38
  • 1