Questions tagged [tesla]
10 questions
9
votes
2 answers
240 V Car charging circuit
I have a 90 amp breaker outside my house, which then runs to my breaker box within my garage. My A/C and range are on separated external breakers.
I want to install a 240 V charger for a Tesla within my garage and am seeing many conflicting…
DevelopingDeveloper
- 243
- 2
- 7
3
votes
2 answers
Is there a problem oversizing a circuit for a car charger?
I am wiring a Tesla wall connector with #6 gauge THHN in conduit and installing a 60 amp breaker to allow for a max 48 amp charge. If I only need a 48 amp charge every so often and choose to continually set the car charger to charge using a lower…
john s
- 149
- 3
- 8
2
votes
3 answers
EV charger installation setup
I have purchased a new Tesla model Y and figuring out options to install a home charger in my garage.
Issue: I live in MA and I do not have a basement or crawl space. My circuit panel is on the ground level in a room adjacent to garage but at least…
ASR
- 21
- 1
2
votes
4 answers
Leviton 14-50 Works, Bryant 14-50 Doesn't - Same Wiring
Question for you all. Kinda at my wits end with this one, it just doesn't make any sense to me.
I have had the issue of my Tesla charger dropping down to 16 amps from 32 amps after 30 minutes due to high outlet temperature. Turns out the usual…
amgdart
- 61
- 5
1
vote
1 answer
EVSE terminal torque specs and associated wire size
For installation of a Tesla Gen 3 EVSE the manual requires the terminal screws be tightened to 50 lbf.in torque and recommends wire from #12-#4 gauge with #6 gauge wire used for a maximum possible charge.
Since wire with a smaller diameter than #6…
stan li
- 11
- 1
1
vote
2 answers
Installed Tesla gen 3 home charger with 60amp breaker and car pulling 48 amps. The conduit from charger to power panel is approx 4 ft
The conduit gets so hot you can't keep touching it. The certified electrician used #6 THHN. should #4 wire be used?
Gary D. Giebel
- 11
- 1
- 2
1
vote
1 answer
GFCI breakers in a subpanel trip when a main panel circuit powering a Tesla wall charger is being used
Four years ago we installed a 50A 240V circuit to power a hot tub. There is a standard 50A breaker in the main service panel (a 1990's vintage 200A Murray panel), with 4 wires (L1, L2, neutral and ground) to an Eaton subpanel (located about 50 ft…
dponti
- 11
- 4
1
vote
2 answers
Should I run conduit or Teck cable for car charging?
I am planning on getting an electric car in the near future - ordered delivery early next year. I park the car on the city street in front of my house. The city owns the piece of grass from the street to the side walk and a couple feet from the…
Fresh Codemonger
- 14,459
- 3
- 24
- 57
0
votes
3 answers
What to do with extra wire when connecting Tesla charger
Using Teck90 cable to install Tesla charger. I only need the red, black, and blue wires. Should I just cut the bare copper short and leave it unconnected at both ends? I’m in British Columbia, Canada.
Eryn
- 31
-1
votes
4 answers
14-30 switchable splitter
I have single wall plug NEMA 14-30 which is currently sometimes (rarely) occupied by the drier.
I want to add Tesla Mobile charger with 14-30 adapter (from Tesla) to the same outlet of course not at same time.
I do not want to have to unplug one to…
DIY75
- 20,686
- 3
- 23
- 47